Order Aube by Honeywell TI070-3W/U ECONO Switch Programmable Timer Switch, White


The timer works as most people have already discussed in their reviews, and is great because no other timer I have found will control compact fluorescent bulbs (CFL's). However, please be VERY careful wiring it. If you look at the wiring diagram enclosed, the connections are reversed: It shows line connected to load and vice versa. The directions as written in text are correct, but the two are not consistent with each other. I do not know what would happen if you reversed the wires. I am guessing the switch would either not work, or it could be damaged. Please be careful.

A distinction that should be clarified is that this TI070 model must have a load OVER 40 watts in order to function. If you are controlling CFL's (as I am) that is more than 3 bulbs since a 60W incandescent equivalent draws just 13 watts. I actually had to add a fourth bulb to bring the total load from 39 watts to 52 watts (slightly wasteful). However, the TI071 model can handle loads less than 40 watts according to the instructions. But, apparently that model requires a neutral wire, which the TI070 model does NOT.

So, to summarize:

TI070 model: Needs a load of at least 40 watts, does NOT need a neutral wire connection
TI071 model: Can handle a smaller load below 40 watts, DOES need a neutral wire connection

Hope this is helpful!Get more detail about Aube by Honeywell TI070-3W/U ECONO Switch Programmable Timer Switch, White.